AND
AIR CONDITIONING
INTRODUCTION
The Definition
Psychrometric is the study of the properties of mixtures of air and
water vapor
The Importance
Very useful in carrying out heat
load or cooling load calculations
To select a suitable air
conditioning equipment
To solve any air conditioning
system which operated as not
as expected.
PSYCHROMETRIC MIXTURES
PSYCHROMETRIC MIXTURES
Daltons Law of Partial Pressures
Let
say
the
pressure
of
atmospheric air is 1.013 bar. If the
air temperature is 30oC, then
Ps = 4.2469 kPa.
Thus,
Pa = P Ps = 101.13 - 4.2469
= 96.88 kPa
P = P1 + P2
PSYCHROMETRIC MIXTURES
PSYCHROMETRIC MIXTURES
Dew Point Temperature, TDP
PSYCHROMETRIC MIXTURES
Dew Point Temperature, TDP
30
25
Ps = 3.1698 kPa
PSYCHROMETRIC MIXTURES
Specific Humidity or Moisture Content
ma V / a s
water vapor present in the air and is measured in kg per kg of dry air
(kg/kg of dry air).
Ru
T
Ma
ma
paVMa
RuT
and
psV ms
Ru
T
Ms
ms
psVMs
RuT
PSYCHROMETRIC MIXTURES
Thus,
ms PsVMs
ma
RuT
PaVMa
PM
18.016Ps
s s
RuT
PaMa 28.966Pa
0.622
622
Ps
kg / kg d.a.
Pa
Ps
g / kg d.a.
Pa
Then
0.622
Ps
Ps
kg / kg d.a 0.622
kg / kg d.a.
Pa
P Ps
Example 1
Given the moisture from air begins to condense on a metal container when its
temperature is 10 oC. Find
a) Partial pressure of the water vapour
b) Moisture content of the air in the room with p = 101.325 kPa.
Solution
a) From water properties table, TDP = 10 oC, PS = 1.227 kPa
b) 0.622
pw
1.227
0.622
0.007624 kg / kg d.a.
p pw
101.325-1.227
PSYCHROMETRIC MIXTURES
Relative Humidity (RH)
Denoted by or RH
Define as the ratio of the actual mass of the water vapor, ms in a given
volume of moist air to that which it would have if it were saturated at
the same temperature.
ms PsV RT Ps
mg PgV RT Pg
From V m , then,
From, 0.622
From,
ps
pg
V s g
V g s
ps
pa
ps
pa
0.622 ps
ps pg , then 0.622
pg
pa
PSYCHROMETRIC MIXTURES
Relative Humidity (RH)
PSYCHROMETRIC MIXTURES
Percentage of Saturation or
Degree of Saturation
Denoted by
Defined as the ratio of the specific humidity, of the mixture to the
specific humidity of the mixture when saturated at the same
temperature. Thus
ps
0.622
p ps
p p pg
pg
g
pg p ps
0.622
p pg
pg
p pg
and g 0.622
g
g
0.622 pg
p pg
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
Example 2
The air supplied to a room of a building in winter is to be at 15oC and have a
percentage relative humidity of 60%. If the barometric pressure is 1.01326 bar,
calculate the specific humidity. What would be the dew point under these
conditions?
Solution
From water properties table, at 15oC, Pg = 1.7051 kPa
ps
Ps pg 0.6 1.7051 1.02306 kPa
pg
0.622
ps
1.02306
0.622
0.00634 kg / kg d.a.
p ps
101.326-1.02306
If the air is cooled at constant pressure, the vapour will begin to condense at the
saturation temperature corresponding to 1. 02306 kPa. The the Tdp
1.02306 0.8721
o
Tdp
10 5 5 7.12 C
1.2276 0.8721
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
Example 3
If air at the condition of Example 2 is passed at the rate of 0.5 m3/s over a cooling coil which
is at a temperature of 5oC, calculate the amount of vapor which will be condensed. Assume
that the barometric pressure is the same as in Example 2 and that the air leaving the coil is
saturated.
Solution
pa p ps 101.326 1.02306 100.303 kPa
pV
100.303 0.5
ma a
0.6067 kg/s
RaT 0.287 15 273
1 ms ma ms1 1 ma 0.00634 0.6067 0.003846 kg/s
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
Example 3
After passing the cooling coil, = 1, (saturated) then ps = pg. For this condition and at 5oC,
Pg = 0.8721 kPa
2 0.622
ps
0.8721
0.622
0.005400 kg / kg d.a.
p ps
101.325 - 0.8721
PSYCHROMETRIC MIXTURES
Psychrometric Chart
PSYCHROMETRIC MIXTURES
Advantages of using the
Psychrometric Chart
If all the values are calculated manually using the formulae, it
takes lots of time, but with psychrometric chart these values
can be found within seconds or minutes.
With psychrometric chart we can easily find out the present and
the final condition of the air. Say if the air is cooled from 100oF
to 75oF, all we have to do is draw the horizontal line to locate
the initial and final condition of the air.
Psychrometric chart is very useful in carrying out heat load or
cooling load calculations.
PSYCHROMETRIC MIXTURES
Lines on Psychrometric Chart
PSYCHROMETRIC MIXTURES
Lines on Psychrometric Chart
Relative Humidity,
%
Saturation Line
Dry Bulb Temp, oC
Sensible
Heat
Factor
Specific Volume,
m3/kg
Specific Entalpy,
kJ/kg
PSYCHROMETRIC MIXTURES
Specific Enthalpy of Moist Air, h
According to Gibbs Law, the enthalpy of an ideal gas is the summation of
the enthalpies of the constituents.
Thus the enthalpy of moist air, h is equal to the sum of the enthalpies of dry
air and water vapor,
mh ma ha ms hs
hs hg c ps Ts Tg at ps
hg and cps can be taken as 2500 kJ/kg and 1.88 kJ/kgK respectively, thus
hs hg c ps Ts Tg 2500 1.88 Ts Tg
PSYCHROMETRIC MIXTURES
Specific Enthalpy of Moist Air, h
The enthalpy of the mixture per unit mass of dry air can be expressed as,
h c pT hg c ps T Tg at ps
mac pa
ms c ps
m
m
Specific heat capacity of mixture per unit mass of dry air,
mc
c pma c pa s ps c pa c ps
m
cpa = 1.005 kJ/kgK and cps = 1.88 kJ/kgK
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
Room design
condition
Air entering
the room
QS
h h
Sensible heat load
x 1
Total heat load
QS QL h2 h1
m2 m3 m4 m3 m4 m2
m2 h2 m3 h3 m4 h4
m2
m4 m2
h
m 2 m
h3 h4
4
4
Defining r as the mass flow of dry air
recirculated air per unit mass of dry air
supplied to the room, m2 / m4 ,
rh2 1 r h3 h4 r
h3 h4
h3 h2
3 4
3 2
h3 h4 3 4 line 3 - 4
h3 h2 3 2 line 3 - 4
Contac factor
line 5 - A
line 4 - A
line 4 - 5
line 4 - A
EXAMPLE 15.3
An air conditioned room is to be maintained at
18oC and percentage saturation 40%. The
fabric heat gains are 3000 kW and there are a
maximum of 20 people in the room at any
time. Neglecting all other heat gains or
losses, calculate the required volume flow
rate of air to be supplied to the room and its
percentage saturation when the air supply
temperature is 10oC.
Room design
condition
Air entering
the room
Data :
Sensible heat gain = 3000 + (20 x 100)
= 5000 W
Latent heat gain = 20 x 30 = 600 W
EXAMPLE 15.3
From air water properties table at 18oC, pg2 = 0.02063 bar
0.622 pg 0.4 0.622 0.02063
0.00517
p p
g
1.01325
0.02063
g
1 2
600
ma 2533.9
where hg = hg at
T2 = 2533.9 kJ/kg
600
0.2368
0.00517
ma 2533.9
ma
5000
8.04 15.041
Room design
condition
Air entering
the room
EXAMPLE 15.3
Combining 1 0.00517
0.2368
ma
and
ma
5000
8.04 15.041
0.2368
8.04 15.041 1 0.00479
5000
5000
ma
616.4 kg/s
8.04 15.04 0.00479
1 0.00517
1 0.622
ps1
0.622
0.622
pa1
1
0.00479
pa1
ps1
p pa1
0.622
0.00479
1.01325 pa1
EXAMPLE 15.3
pa1 1.00551 10 2
RT 1
a1
1.238 kg/m 3
p
RT1
0.287 283
m V Va1
616.4
498 m 3 / s
1.238
100a1 p pg1
0.622 pg1
0.893
QS QL 5600
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
EXAMPLE 15.4
Air at 1oC dry bulb and 80% and
percentage saturation mixes adiabtically
with air at 18oC dry buld and 40%
percentage saturation in the ratio of 1 to 3
by volume. Calculate the temperature and
percentage saturation of the mixture.
Take the barometric pressure as 1.01325
bar.
3
T1=1oC
T3 T2=18oC
2
3
1
EXAMPLE 15.4
Given :
ma1
V2
3
V1
Va1
a1
and ma2
Va2
a2
2.82
ma1 Va1 a2 1 0.83
ma1
ma1
line 3 2
0.262
line 1 2 ma1 ma2 ma1 2.82ma1
T2 T3
0.262 T3 18 0.262 18 1 13.6 o C
T2 T1
By locating the point 3, T3 can be
determined, T3 = 13.6oC
T1=1oC
T3 T2=18oC
2
3
1
EXAMPLE 15.5
An air conditioning plans is designed to maintain a room at a condition of 20oC
dry bulb and specific humidity 0.0079 when the outside condition is 30oC dry
bulb and 40% percentage saturation and the corresponding heat gains are
18000 W (sensible) and 3600 W (latent). The supply air contains one-third
outside air by mass and the supply temperature is to be 15oC dry bulb.
The plant consists of a mixing chamber for fresh air and recirculated air, an air
washer with chilled spray water with an efficiency of 80% an after heater battery
and supply fan. Neglecting temperature changes in fan and ducting, calculate :
i. The mass flow rate of supply air necessary
ii. The specific humidity of the supply air
iii. The cooling duty of the washer
iv. The heating duty of the after heater
Use the psychrometric chart assuming the barometric pressure is 1.01325 bar.
EXAMPLE 15.5
Solution :
Points 2 and 3 can be fixed since the conditions are known.
Fresh air is to be one-third by mass of the total air to the room, thus point 4
is 1/3 from point 2.
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
EXAMPLE 15.5
Sensible heat ratio
QS
18000
QS QL 18000 3600
0.833
5
Line 4 5
0.8 4
Line 4 A
4 A
A 4
4 1
0.8
0.0089
0.0089 0.0075
0.8
0.00715
Point 5 is fixed by joining points 4 and A, where this
line cuts the horizontal line through point 1, T5 =
12oC.
Mohd Kamal Ariffin, Faculty of Mechanical Engineering, UTM, 2014
EXAMPLE 15.5
i)
ii) From the chart, the specific humidity of supply air = 0.00745 kg/kg d.a.
iii) From the chart, h4 = 46.2 kJ/kg and h5 = 31.1 kJ/kg
Cooling load of the coil ma1 h4 h5 3.43 46.2 31.1 51.8 kW