Bar Bending
The process of bending reinforcing steel into shapes required for reinforced concrete
construction.
Bar bending schedule (or schedule of bars) is a list of reinforcement bars, a given RCC
work item, and is presented in a tabular form for easy visual reference. This table
summarizes all the needed particulars of bars – diameter, shape of bending, length of
each bent and straight portions, angles of bending, total length of each bar, and
number of each type of bar. This information is a great help in preparing an estimate
of quantities.
Here’s the procedure to arrive at the length of hooks and the total length of a given steel
reinforcement.
Advantages of Bar bending schedule (BBS) :
When Bar bending schedule is available, cutting and bending of reinforcement can be done at
factory and transported to site. This increases faster execution at site and reduces construction
time and cost due to less requirement of workers for bar bending. Bar bending also avoids the
wastage of steel reinforcement (5 to 10%) and thus saves project cost.
1. Using bar bending schedule for when used for Fe500, it saves 10% more steel
reinforcement compared to fe415.
6. Bar bending schedule can be used for reinforcement cutting, bending and
making skeleton of structural member before it can be placed at the required
position. Other activities such as excavation, PCC etc can proceed parallel with
this activity. So, overall project activity management becomes easy and reduces
time of construction. It becomes helpful in preventing any damages due to
construction time overrun.
8.Bar bending schedule provides the steel quantity requirement much accurately and thus
provides an option to optimize the design in case of cost overrun.
9.It becomes easy for site engineers to verify and approve the bar bending and
cutting length during inspection before placement of concrete with the use of bar
bending schedule and helps in better quality control.
10.It enables easy and fast preparation of bills of construction works for clients
and contractors.
12.With the use of bar bending schedule, mechanization of cutting and bending of
reinforcement can be done, again reducing the cost and time of project and
dependency on skilled labor requirement. It also improves the reliability on
accuracy of bar cutting and bending.
13.When mechanized bar cutting and bending is used, the cost of reinforced
concrete work per unit reduces and helps in cost optimization of construction
project..
Here’s the example of Bar bending schedule (BBS) of “Floor Slab Reinforcement”.
In Bar bending schedule, the bars are organized for each structural units (Beams or
columns or slabs or footings etc) and detailed list is prepared which specifies the Bar
location (Bar in footings, slabs, beams or columns), Bar Marking (to identify the bar in
accordance with the drawing), Bar Size (length of the barused), Quantity (No. of Bars
used), Cutting length, Type of Bend and Shape of the bar in reinforcement drawings.
How BBS Changed from 1950-2019:-
From 1950 to 2019 lots of modifications and enhancements happening in our world. In
1950, three-storeyed buildings are high rise buildings now we are constructing a
building with 200 floors+. There is a massive growth in the construction industry. Due
to the vast increase in world population demands increased facilities, more need for
space and more construction.
Father of Estimation B.N. Datta has given certain recommendations for the usage of
steel in different components of buildings. But, he didn’t mention any values if we use
more bars in a single structural member.
Bar Bending Member Percentage
(If you are viewing the below table through mobile, scroll horizontally for a clear view)
S.No. Particulars Result
Ex:If length of bar is 12m with 10mm Dia then , Weight of bar = D2/162
From above fig, length of hook = [(Curved Portion) + 4d] = [(4d+d)+4d] = 9d Hook
Therefore Total Cutting length = L+18d (d is the Diameter of a bar) Hope, now
2. Bend Length:-
The Bend length calculation is different for Cranked bars (bent up bars) and bends at
corners.
The bars are usually cranked in Slabs and bars are bent at corners in Stirrups or ties.
From above fig, There are 3 bends which are bent at an angle of 90 0 and two bends are
bent at an angle of 1350
Total bend length = 3 x 900 Bend length + 2 x 1350 Bend length = 3 x 2d + 2 x 3d = 12d =
12 x 8 = 96mm
Learn more:How to find the cutting length of stirrups in Columns and Beams for
different shapes
Below table represents the total length of bar calculation for different types of bar
shapes.
Below table represents the total length of bar calculation for different types of bar
shapes.
(If you are viewing the below table through mobile, scroll horizontally for a clear view)
Total Total
Total Length of
Bar Shapes
Length Bend
Bar
of Hooks
Straight Bar Two No l + 18D
Hooks bend
= 9d +
9d
= 18d
the below picture on top floor of the building? We generally project some length of
Bar on the last floor i.e., 50D. It is used for further construction purpose. (Constructing
a new floor)
BBS of Column
Lapping can be defined as the overlapping of two bars side by side to upto the design
length. Usually, the stock length of steel bars is limited to 12m. This is for easy
transportation of steel bars to the construction site. For example, imagine there is a
need to build a 100ft tall column. But it’s not practically available.Hence the bars are
cut every second story.
steel bars overlapped
Then the tension forces are required to be transferred from one bar to the other bar at
the location of discontinuity of the bar. So the second bar is kept closely to the first bar
and overlapping is done. This amount of overlapping between two bars is called “lap
length”. Lapping is usually done where minimum bending stress is encountered. In
general, lap length is 50d which means 50 times the bar diameter, if both bars are of
same diameter.
The straight length of lapping of bars shall not be less than 15d or 20cm. Lap
Length in Compression:
The lap length is equal to the development length calculated in compression but not
less than 24d.
For Different Diameter Bars:
When the bars of different diameters are to be spliced, the lap length is calculated
considering the smaller diameter bar.
Lap Splices
Lap splices should not be catered for the bars which are having diameter greater than
36 mm. In such cases, welding should be considered. But if welding is also not feasible
in some conditions, then lapping may be allowed for the bars larger than 36 mm
diameter. But along with lapping, additional spirals of 6 mm should be provided
around the lapped bars.
Lap splice length in a footing Lap length for concrete of 1:2:4
Nominal mix:
The Lapping length in tension (MS bar – mild steel bar) including anchorage value is
58d. So eliminating the anchorage value, the lap length = 58d – 2*9d = 40d. (Where
9d = hook allowance up to 25 mm and k=2)
Lap length for M20 concrete:
Columns – 45d
Beams – 60d
Slabs – 60d
This infers that if we need to lap 20 mm diameter column bars, a minimum lap of 45 *
20 = 900 mm is provided.
The Indian bible (IS456) says that the development length Ld of any bar shall be given
by the following relation
Although technically speaking development length is not the same as splice length,
they are essentially represent the same quantity of reinforcement to be extended in
order to achieve complete transfer of stresses.
Now, the code also gives us thumb rules for splice lengths:
1. For bars in flexural tension (bottom bars in most non-cantilever beams), use
'Ld' from above or 30 times the bar diameter, whichever is more.
You could use the same for slabs.
2. For bars in compression (typically the ones in columns) use the 'Ld' from the
above relation. Except that in compression, our bond stress can be increased by
25% so, effectively, take Ld in compression as Ld/1.25
3. However, the above Ld in compression must not be less than 24 times the
diameter of the rebar.
Also, please refer the code for various other specification regarding the Ld when
multiple bars are spliced together, when bars of different diameters are spliced, etc.
You may use the following values for M30 grade of concrete for varying grades of steel in flexural
tension:
(Note how the Ld decreases with increase in grade of RCC and how it increases with
increase in the strength of steel used)
Development length can be defined as the amount of reinforcement(bar)
length needed to be embedded or projected into the column to establish the
desired bond strength between the concrete and steel (or any other two
types of material). Fig 1: Development length in Footing. Reinforcing bar
(rebar) comes in lengths up to 60 feet the lap splice, as the name suggests, is
created by overlapping two lengths of rebar, then wiring them together.
From a structural point of view, the most critical aspect of a lap splice is the
overlap length.
Development length
During placing the steel in RC structure if the required length of a bar is not
sufficiently available to make a design length then lapping is done.
Lap length is the minimum length that must be provided if two bars are joined
together such that forces can be transferred safely.
Suppose, we need to build a 100 feet tall column. But practically 100 ft long bar is not
available and it is also not possible to cage. Therefore we need to cut the bars in every
second story. Now, we need to transfer the tension forces from one bar to the other
at the location of discontinuity of bar. So we have to provide the second bar closed to
the first bar that is discontinued and overlapping is to be done. The amount of
overlapping between two bars is known as lap length.
The straight length of lapping shall not be less than 15d or 20 cm. LAP
LENGTH IN COMPRESSION:
In case of bars having different diameter are to be spliced, the lap length is calculated
on the basis of smaller diameter bar.
Otherwise in scenarios where less development length against the required is provided the
structures will be prone to encounter failure due to slippage of joints, bonds, anchors & Laps,
in such cases the bars will not yield first but the failure will happen at joints & laps prior to
yielding of reinforcement bars.
Where,
Ø = nominal dia of reinforcement bar
?s = Stress in bar at the section considered at design load
?bd = Design bond stress
Fig 2: Development length as per IS 1786
The above given formula is used to calculate the required development length in mm for any given
dia of bar, same formula is used for limit state method as well as working stress method. The only
change in calculation in both methods is due to the different value of design bond stress; the
values of design bond for Limit State & working stress are as follows;
Table No 1: Design Bond Stress in Limit State Method
Design Bond Stress in Limit State Method
M40 and
M20 M25 M30 M35 –
above
L = (0.87*f*d)/4t
Where,
L is development length,
f is grade of steel
d is dia of bar
t is bond strength (denoted by tau)
Note :-
Development length of bar is nothing but the extra length of bar require to provide for
development of stress in steel at that section.
At any section whatever stress produced is need to be develop in steel through bond between
steel and concrete. So that the bar will not get pull out of concrete…as one friend give very good
example of finger with grease.
Thats why, when calculating development length need to account bond stress. You can find it out
by equating,
(bond stress × Develop. Length × perimeter of bar) = ( yield stress of steel i.e 0.87*fy)
And bond stress as per IS 456:2000, table given with grade of concrete.
This length again we can say that, length from critical section to tangent to hook of bar plus
anchorage length of bar.