Objective
SRC5,6 & 10 KVA Common Issues
Schneider Electric
Let us look at these issue in detail and corrective action for the same.
Schneider Electric
Schneider Electric
Contd.,
Troubleshooting:
If you notice the above mentioned fault in the field, please do the following: Check the load and ensure that the load is normal Check the Generator output frequency and voltage if available, and ensure that the Genset frequency is between 4753 Hz and ensure that the frequency is not varying abnormally
If the 010 DC Bus OverV fault clears after your restart the UPS, then upgrade the UPS firmware. Please contact your Regional APC tech specialist for the same.
Schneider Electric
Restart the UPS and see if the fault clears. If the fault does not clear, then replace the unit and mention the fault code on the defective service tag.
Schneider Electric
Schneider Electric
Quick Quiz
SRC6000UXI is connected to 16 numbers of 12 Vdc, 65 AH batteries. What is the total external battery AH that needs to be set on the SRC6000UXI display?
Schneider Electric
Schneider Electric
Connect a master device, such as a desktop computer or audio/visual receiver to the Master outlet. Connect peripheral devices such as a printer, speakers, or a scanner to the Controlled by Master outlets.
Schneider Electric 10
Operation
Display interface:
On Line Power-Saving Load Capacity
On Battery Replace Battery Mute System Faults In & Out Automatic Voltage Regulation
Battery Charge
Overload Event
Schneider Electric
11
Operation
Automatic Voltage Regulation (AVR):
AVR compensates for excessively high or low input voltages, without using battery power.
When the AVR symbol is illuminated, the unit is either in Boost or Trim mode.
Schneider Electric
12
Operation
Modes of operation:
Press DISPLAY to scroll through display screens. Online Mode
Input Voltage
On Battery Mode
Estimated runtime in minutes
Power Event Counter Output Voltage Input Voltage Load in Watts Load in % Output Frequency
Counter Estimated run time Load in Watts Load in % Output Voltage Output Frequency
Schneider Electric
13
Configuration
Power-Saving Master & Controlled outlets:
Configure Back-UPS to recognize a Master device and Controlled peripherals. Enable the Power-Saving feature: Press and hold MUTE and DISPLAY simultaneously for two seconds. Unit will beep to indicate that the feature is enabled. Disable the Power-Saving feature: Press and hold MUTE and DISPLAY simultaneously for two seconds Unit will beep to indicate that the feature is disabled.
Setting the Threshold: 1. Ensure your computer is plugged into the Master outlet. 2. Put your computer into Sleep or Standby mode, or turn it OFF. 3. Press DISPLAY and MUTE simultaneously for six seconds, until the leaf icon flashes three times and the unit beeps three times. 4. Back-UPS will now recognize the threshold level of the Master device and save it as the new threshold setting.
Schneider Electric
14
1. Full Time Mode: Press and hold DISPLAY for two seconds. The display will illuminate and the Back-UPS will beep to confirm the Full-Time mode. 2. Power-Saving Mode: Press and hold DISPLAY for two seconds. The display will go dark and the Back-UPS will beep to confirm the Power-Saving mode. While in Power-Saving Mode, the display will illuminate if a button is pressed, it then goes dark after 60 seconds of no activity.
Schneider Electric
15
Configuration
Adjusting UPS sensitivity:
Adjust sensitivity of the UPS to control when it will switch to battery power.
1. Ensure the unit is connected to utility power, but is OFF. 2. Press and hold the POWER button for six seconds. 3. LOAD CAPACITY bar will flash on and off, indicating that the unit is in programming mode. 4. Press POWER again to rotate through the menu options. 5. Stop at selected sensitivity. The unit will beep to confirm the selection.
Schneider Electric
17
On-Battery Overload On-Battery Output Short On-Battery Xcap Overload Clamp Short Charge Fault Relay Welding Temperature Fan Fault Internal Fault
18
Schneider Electric
Function Buttons
Schneider Electric
19
BR1000G-IN
Schneider Electric
NPF Discussion
Smart UPS NPFs are a big concern for the Company. We are incurring huge cost on Smart UPSs which are becoming NPFs at our repair center. Please discuss any issues with APC regional tech specialist and clarify the issue before replacing any units which are more than 5 KVA. Please ensure to fill the Defective Service Tags with actual fault so that NPFs can be avoided with the respect the fault code.
Schneider Electric
22
DOA Failures
We request you to get an email approval from your RTS if you notice any DOA failures of above 5 KVA UPSs in the field. You can discuss the issue over the phone with RTS, and get an email approval from RTS before replacing the unit.
Schneider Electric
23
THANK YOU
Schneider Electric
25